dryer cord
Click here for Top Ten Discussions. CLICK HERE for Q & A Homepage
Receive Free Rental Owner Updates Email:  
MrLandlord Q & A
     
     
dryer cord (by small potatoes [NY]) Jan 25, 2022 10:07 AM
       dryer cord (by LisaFL [FL]) Jan 25, 2022 10:23 AM
       dryer cord (by LisaFL [FL]) Jan 25, 2022 10:33 AM
       dryer cord (by LisaFL [FL]) Jan 25, 2022 10:38 AM
       dryer cord (by MikeA [TX]) Jan 25, 2022 10:55 AM
       dryer cord (by Robin [NY]) Jan 25, 2022 11:24 AM
       dryer cord (by Still Learning [NH]) Jan 25, 2022 12:02 PM
       dryer cord (by small potatoes [NY]) Jan 25, 2022 12:06 PM
       dryer cord (by MikeA [TX]) Jan 25, 2022 12:25 PM
       dryer cord (by Jason [VA]) Jan 25, 2022 12:37 PM
       dryer cord (by LisaFL [FL]) Jan 25, 2022 12:44 PM
       dryer cord (by don [PA]) Jan 25, 2022 2:46 PM
       dryer cord (by Robert,OntarioCanada [ON]) Jan 25, 2022 2:57 PM
       dryer cord (by Robert J [CA]) Jan 25, 2022 6:21 PM
       dryer cord (by Pmh [TX]) Jan 25, 2022 6:21 PM
       dryer cord (by small potatoes [NY]) Jan 25, 2022 11:18 PM
       dryer cord (by Robert,OntarioCanada [ON]) Jan 25, 2022 11:31 PM
       dryer cord (by Dave [CA]) Jan 26, 2022 6:49 AM
       dryer cord (by Wilma [PA]) Jan 26, 2022 12:53 PM


dryer cord (by small potatoes [NY]) Posted on: Jan 25, 2022 10:07 AM
Message:

tenant called and GE wouldn't install a new dryer because there is a 3 prong outlet. Their claim is that the new dryer requires a 50 amp circuit w/ a 4 prong outlet. And that if a 3 prong plug is installed on their dryer it might short out the dryer and void the warranty. They further told them it was a range outlet. I have had tenants use this for a dryer for over 15 years. Isn't this a non-issue? The box stores ask you all the time what cord you need. I'm reluctant to tell the tenant to do this when GE told them otherwise. Should I recommend they buy a dryer elsewhere? I don't know why a 4 prong outlet on the service line for 30 amps isn't sufficient.

--24.194.xxx.xx




dryer cord (by LisaFL [FL]) Posted on: Jan 25, 2022 10:23 AM
Message:

Never heard of such a thing. Dryer’s use a 30 amp breaker, either 3 or 4 prong.

I suspect the installer doesn’t know what they’re talking about. I would not change my breaker for some special needs anomaly dryer. Your plug is to standard code.

I’d probably ask for the make/model of their dryer and research it for myself before telling them no because they are likely misinformed. --24.96.xx.xxx




dryer cord (by LisaFL [FL]) Posted on: Jan 25, 2022 10:33 AM
Message:

Just did a quick google search which took me to the GE dryer electrical requirements for all GE/Hotpoint dryers. 30 amp is it. --24.96.xx.xxx




dryer cord (by LisaFL [FL]) Posted on: Jan 25, 2022 10:38 AM
Message:

What they were recommending it sounds like is they change out the 30 amp 3 prong plug to a 30 amp 4 prong dryer plug which newer homes require because it has a build in ground (or something like that). But the existing 3 prong plug will work just fine and is what most people have anyway.

If you change it, it will require future tenants to have to change their cords. --24.96.xx.xxx




dryer cord (by MikeA [TX]) Posted on: Jan 25, 2022 10:55 AM
Message:

I would ask for the model number of the dryer and look it up on-line or ask them to send you a photo of the plate on the dryer with the specs. I have never seen a 50 Amp dryer and to do so would certainly go against the building code so pretty sure a manufacturer wouldn't do that. Dryers are 30 amp and Stoves are 50 amp by code.

That said there are 30 amp and 50 amp 3 prong and 4 prong outlets, each has a different configuration so you can't plug into the wrong one. Here's a picture of each so you can identify it: www.askmediy.com/220-volt-plugs-receptacles-configurations/ . The code changed around 1990 in most places. Before, the 3 prong was code, after, the 4 prong with an extra ground was code. The 3 prong plug will be grandfathered so no need to pull new wire and replace it. You can buy a 3 prong to 4 prong adapter or replace the cord on the dryer with the appropriate 3 prong cable if it comes with a 4 prong cable. --209.16.xx.xxx




dryer cord (by Robin [NY]) Posted on: Jan 25, 2022 11:24 AM
Message:

30 Amp for dryer

50 Amp for range

Just swap out the old for the new. You are okay. --207.241.xxx.xxx




dryer cord (by Still Learning [NH]) Posted on: Jan 25, 2022 12:02 PM
Message:

I vaguely remember something like this with one tenant that brought their w/d to the unit. I don’t remember the outcome but I’m guessing my electrician told me to have them change their cord. --75.67.xxx.xxx




dryer cord (by small potatoes [NY]) Posted on: Jan 25, 2022 12:06 PM
Message:

I got clarification from the tenant. GE installer looked at the outlet and said it is a range outlet, which led them to assume it is a 50A circuit. I verified the circuit is 30A.

LisaFL, I just went through this in a different unit. The new models have 4 prong plugs standard. I will update the outlet to 4 prong and when GE returns they cannot complain it doesn't meet their needs. I'd rather not inconvenience the tenant and get into a pissin match when they return w the dryer, since I'd rather not be there anyway. --24.194.xxx.xx




dryer cord (by MikeA [TX]) Posted on: Jan 25, 2022 12:25 PM
Message:

Unfortunately you can't legally just change the outlet. The code requires a 2nd ground wire so you will have to have another wire pulled to a grounding source/breaker panel.

The simplest is to buy the adapter so their 4 prong plug can plug into the 3 prong outlet. Most of them are a cabe about a foot long that has the appropriate plugs on either end. That will keep you from having to pay an electrician to rewire it. --209.16.xx.xxx




dryer cord (by Jason [VA]) Posted on: Jan 25, 2022 12:37 PM
Message:

The national electric code changed around ‘98 that changed the requirements from a three wire to four. It’s perfectly acceptable to have a three wire receptacle.

If it was mine, I’d just put a 50 amp cord on it and call it a day. Your other option would be to change the dance receptacle out to a three wire dryer receptacle. --50.202.xxx.xx




dryer cord (by LisaFL [FL]) Posted on: Jan 25, 2022 12:44 PM
Message:

Mike is correct. But the simple way to do is to put a 3 prong cord on the dryer and plug it into the existing plug.

I have a collection of them and swap them out for people all the time if the one they show up with is the wrong one. I have a tenant who is an electrician and he charges them a few bucks to do it for them. --24.96.xx.xxx




dryer cord (by don [PA]) Posted on: Jan 25, 2022 2:46 PM
Message:

The wire for a 50 amp circuit (6 or 8 gauge) is heavier than for a 30 amp circuit. I don't see why a 30 amp receptacle could not be attached to it. You would not even have to change the breaker to 30amp because the wiring is rated at 50amp, although you could if you wanted to.

I have never heard of a 50 amp dryer circuit. --73.141.xxx.xxx




dryer cord (by Robert,OntarioCanada [ON]) Posted on: Jan 25, 2022 2:57 PM
Message:

It is easy to buy a four pin receptacle then a box where install. The only other option is buy a natural gas clothes dryer which plugs into a 120 VAC outlet as natural gas is used for heat. Here there was never a three pin outlet for dryers or stoves where always a four pin. In the house and apartment buildings used only natural gas commercial clothes dryers. --68.69.xxx.xxx




dryer cord (by Robert J [CA]) Posted on: Jan 25, 2022 6:21 PM
Message:

I am a landlord, contractor and electrician. There is a communications gap between you, your tenant and the appliance provider. A few things should have been discussed but weren't.

Like when it comes to a dryer, here are a few questions:

#1 Is the dryer Natural Gas, Propane or Electric (120 volts or 240 volts)?

#2 Does the vent pipe discharge from the back or the sides (Which side)?

#3 Which direction does the dryer door open? From right to left or from Left to right?

The owner should inform their tenant what type of dryer will fit in the home. Like a 240 volt electric dryer with a 3 prong plug. Rear venting.

--47.155.xx.xxx




dryer cord (by Pmh [TX]) Posted on: Jan 25, 2022 6:21 PM
Message:

I just had this same situation changing out a dryer. all you have to do is unscrew back plate and screw in new cord with the new prongs from 4 to 3. you do NOT need to buy a new dryer. It cost me $35 for the new cord. Lowe’s or HD. --107.77.xxx.xxx




dryer cord (by small potatoes [NY]) Posted on: Jan 25, 2022 11:18 PM
Message:

MikeA, my electrician said I could update the outlet on a 30 Amp line w just swapping the outlets. My circuit is 30 amp.

The only item I saw on HD (nothing in store either) is an adapter that has an additional grounding wire that has to be inserted into the ground pin on a standard outlet (15 or 20A).

Robert J, yes lots of miscommunication. It would be nice if the tenant informed me about the install. The dryer is electric, the vent is in the lower right corner. The GE guy saw this, but only raised a concern about the outlet. Door swing either way- no problem.

. --24.194.xxx.xx




dryer cord (by Robert,OntarioCanada [ON]) Posted on: Jan 25, 2022 11:31 PM
Message:

The purpose of the ground is safety where if the metal part of the dryer becomes the ground will trip circuit breaker or fuse will open protecting people. A electric dryer uses 240VAC for the heating elements and 120 VAC for motor and timer. From red to black 240 VAC then red or black to white 120 VAC. While grounding dryer will work it will not be up to electrical code. Safety is more important then saving a dollars. Three wire receptacles for dryers or stoves were never used here where all the receptacles are four pins. --68.69.xxx.xxx




dryer cord (by Dave [CA]) Posted on: Jan 26, 2022 6:49 AM
Message:

A 240 volt dryer is two hot s and a neutral.

The neutral goes back to the panel.

Although the neutral bar and the ground bar at the panel are separate , they both effectively go to ground, don't they .??

The panel ground goes to. Ground rod at the property and the panel neutral goes to ground at the power plant --172.250.xx.xxx




dryer cord (by Wilma [PA]) Posted on: Jan 26, 2022 12:53 PM
Message:

Following - we're going through this question ourselves with our 1970s era home and the need to reroute the 240V stove wire. --98.115.xxx.xxx





Reply:
Subject: RE: dryer cord
Your Name:
Your State:

Message:
dryer cord
Would you like to be notified via email when somebody replies to this thread?
If so, you must include your valid email address here. Do not add your address more than once per thread/subject. By entering your email address here, you agree to receive notification from Mrlandlord.com every time anyone replies to "this" thread. You will receive response notifications for up to one week following the original post. Your email address will not be visible to readers.