water heater (by Mark [IL]) Nov 23, 2020 8:43 AM
       water heater (by Carolyn [MO]) Nov 23, 2020 9:23 AM
       water heater (by Hoosier [IN]) Nov 23, 2020 9:46 AM
       water heater (by Robert,OntarioCanada [ON]) Nov 23, 2020 10:55 AM
       water heater (by Oregon Woodsmoke [ID]) Nov 23, 2020 10:59 AM
       water heater (by BRAD 20,000 [IN]) Nov 23, 2020 11:22 AM
       water heater (by RobertOntarioCanada [ON]) Nov 24, 2020 1:08 AM
       water heater (by Mark [IL]) Nov 24, 2020 9:01 AM
       water heater (by Hoosier [IN]) Nov 24, 2020 10:45 AM
       water heater (by Robert,OntarioCanada [ON]) Nov 25, 2020 11:52 AM


water heater (by Mark [IL]) Posted on: Nov 23, 2020 8:43 AM
Message:

12 unit building. I have a 75 gal water heater. It drips water on the burners…not too much but it drips …and I am not sure it is normal. Damper shuts off at times. I need to gently touch the black box attached on the side of the damper to “wake it up”..then it opens. Do you think that water on the burners “is normal” ? maybe it has something to do with damper closing down ? the heater is maybe 10 months old --24.13.xxx.xxx




water heater (by Carolyn [MO]) Posted on: Nov 23, 2020 9:23 AM
Message:

If if is only 10 months old it probably is under warranty. You could check with the warranty and get info about whether this is normal and OK or whether someone from the warranty co needs to come and take a look. --136.34.xxx.xxx




water heater (by Hoosier [IN]) Posted on: Nov 23, 2020 9:46 AM
Message:

Not sure what you mean. Gas? You have a water heater with more than one burner? Even on a gas unit, burner is usually difficult to see. Explain please. --99.92.xxx.xxx




water heater (by Robert,OntarioCanada [ON]) Posted on: Nov 23, 2020 10:55 AM
Message:

What happens when the consumable rod is consumed then the glass lining on the tank starts to rust thorough where the hot water tank has to be replaced. If the building has forced hot water boilers then it is better to install a indirect hot water which is stainless steel then is going to outlast the disposable direct fired hot water tanks. While more expensive upfront but more efficient as the stand by loss is less the one degree per hour where a direct fired tank will lose 7 to 12 degrees per hour up the chimney when no hot is being used. Take a flashlight then see if the tank is leaking. --64.228.xx.xx




water heater (by Oregon Woodsmoke [ID]) Posted on: Nov 23, 2020 10:59 AM
Message:

I'd normally say it is a leak in the tank, which means full replacement, but if the heater is only 10 months old, it is probably a loose fitting.

That should still be under warranty so call the company that installed it and make them come out and fix it. --76.178.xx.xx




water heater (by BRAD 20,000 [IN]) Posted on: Nov 23, 2020 11:22 AM
Message:

Mark,

Condensation? When new WHs are first filled with cold water and heat is applied, condensation will make a big puddle.

75 gallons does not sound large enough for 12 showers every morning. Could it be the hot water is all used and the tank has refilled with cold water? Heat on the cold water will make condensation again.

Also check the water fittings on the top or sides. They might be leaking down along the sides of the tank, inside the outer shell.

BRAD --73.102.xxx.xxx




water heater (by RobertOntarioCanada [ON]) Posted on: Nov 24, 2020 1:08 AM
Message:

Try to contact manufacturer where check all fittings for leaks. In most apartment buildings the demand for hot water is in the morning then in the evening from 4 pm to 7 pm where people have showers or baths. A direct fired hot water tank will be working at maximum capacity depending on BTU output. As long as there significant amount of water then the tank maybe working within specifications. If want a long life then after two years inspect then if anode rod is worn replace. Once the anode is consumed then the glass lining of the hot water wears where the hot water tank rusts through. Most commercial hot water tanks have a access clean out where should be removed then inspect with the gas off to remove any sediment as sediment acts as insulator where heat transfer is less then then more natural gas consumption. For efficiency, hot water output and life expectancy a indirect hot water tank is a better option as the boilers are used where the immersion coil transfer heat at lower temperature which means less scale. Boilers have greater heat output then a direct fired hot water tank which means more hot water. In the mean time it is best to get the maximum life out of the existing tank. --147.194.xxx.xx




water heater (by Mark [IL]) Posted on: Nov 24, 2020 9:01 AM
Message:

That’s the beast I have BRADFORD WHITE D-80T-199-3N 199,999 BTU/Hour Commercial Gas Water Heater. If you google it you will see 5 burners at the bottom. Water drips, hissing. Could be condensation but the damper shut off twice on me. Not sure why I need damper anyways. Good point on fittings. I did not spot any leaks though --24.13.xxx.xxx




water heater (by Hoosier [IN]) Posted on: Nov 24, 2020 10:45 AM
Message:

Ok so that explains the 5 burners and non-sealed combustion chamber...it's a commercial unit. Thanks for clarifying. Keep us posted on final resolution. --99.92.xxx.xxx




water heater (by Robert,OntarioCanada [ON]) Posted on: Nov 25, 2020 11:52 AM
Message:

The vent damper prevents heat from going up chimney when the water heater is not firing where the efficiency of the water heater is improved. Most newer cast iron gas boilers have intermittent pilot ignition along with vent damper that improves efficiency. In the boiler room it is possible to improve efficiency by installing pipe insulation on all the heating and hot water pipes which is a inexpensive upgrade where over time will get the money back. Soon the only water heaters sold will be the high efficiency type which extract heat from a secondary heat exchanger like a high efficiency boiler or furnace where the temperature of the exhaust gas is lower where can power vented directly through the wall. Boiler rooms are always warm where if installed a water heater that extract heats from surrounding air would work well where the hot water would be heated before going into the gas fired hot water tank. Bradford White water heaters gas fired and indirect are better quality then what is sold at the big box stores where here the water heater rental companies buy the cheapest water heaters, furnaces out there. With copper finned baseboards efficiency can be improved by cleaning out fins with a air compressor then installing reflective tape on top of fins where more heat will go into a room at a lower temperature where the overall temperature of the heating system will be lower as well. --147.194.xxx.xx





Reply:
Subject: RE: water heater
Your Name:
Your State:

Message:
water heater
Would you like to be notified via email when somebody replies to this thread?
If so, you must include your valid email address here. Do not add your address more than once per thread/subject. By entering your email address here, you agree to receive notification from Mrlandlord.com every time anyone replies to "this" thread. You will receive response notifications for up to one week following the original post. Your email address will not be visible to readers.